PostPosted: Tue Jul 25, 2017 1:22 pm 
Offline
Tadpole

Joined: Tue Jul 25, 2017 1:10 pm
Posts: 2
Hi,
My 2009 Vista 338 AC unit runs for 5 minutes for x3(as manual suggest it will) or so and shows error code that the pressure is too low after the three tries. This is what the manual suggests for the code on the panel. We have checked the freon, replaced the water pump and checked the amount of water is flowing well to the unit.
Does the air intake come from the cabin thru the radiator on the unit?
It's been suggested that the air coming in is too little.
The AC unit has not worked since we bought it, so I don't know if it has worked at all historically.

Any insight is appreciated.


Top
 Profile  
 
PostPosted: Tue Jul 25, 2017 8:25 pm 
Offline
email admin your custom rank

Joined: Sun Jul 05, 2009 5:56 am
Posts: 930
Location: Georgian Bay, Ontario
How did you check the refrigerant level, gauges? Is the circulation fan running? Possible a bad low pressure switch.

_________________
2001 328 Vista "Nauta Dream 2"
AB Inflatable 10AL "Little Dreamer"
2000 248 Vista
1997 225 Sundowner


Mike


Top
 Profile  
 
PostPosted: Tue Jul 25, 2017 9:49 pm 
Offline
Tadpole

Joined: Tue Jul 25, 2017 1:10 pm
Posts: 2
acguy,
Yes i have had the refrigerant level checked with gauges. I was looking for a low pressure switch but this unit doesn't seem to have one. Would it just be electronic?
There is a high one but no low pressure...
the unit does push air thru the system adequately. The AC unit starts to show some frozen condensation on the condenser.
Lake Effects09


Top
 Profile  
 
PostPosted: Wed Jul 26, 2017 3:29 pm 
Offline
email admin your custom rank

Joined: Sun Jul 05, 2009 5:56 am
Posts: 930
Location: Georgian Bay, Ontario
Sounds low on refrigerant, the low pressure switch will be located on the largest line close to the compressor, on an access fitting.
There are only 2 things that will cause frost on the unit after 5min operation, low refrigerant charge or low air flow across the coil

_________________
2001 328 Vista "Nauta Dream 2"
AB Inflatable 10AL "Little Dreamer"
2000 248 Vista
1997 225 Sundowner


Mike


Top
 Profile  
 
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 4 posts ] 

All times are UTC - 6 hours [ DST ]


Who is online

Users browsing this forum: No registered users and 22 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum

Search for:
Jump to:  
Powered by phpBB® Forum Software © phpBB Group