Author:  captain888 [ Sat Mar 10, 2018 12:22 am ]
Post subject:  2009 V358 Generator

I am trying to find out where the Freshwater circulating pump is driven and located on a Kohler 4EFCD Generator.
My gen set starts up runs for about 10 minutes under load then shuts down with an error code HE High Engine temp
I have checked and replaced all saltwater side also cleaned heat exchanger and new thermostat any ideas.
Thanks

Author:  chris268 [ Sat Mar 10, 2018 8:04 am ]
Post subject:  Re: 2009 V358 Generator

Here is a manual, http://www.wilkey.org/blogs/alegrias/Do ... Manual.pdf

I would look at the impeller

Page 13 shows the location and 31 has the info on changing it


Hope this helps, and Good luck!

Author:  Paul358V [ Sat Mar 10, 2018 8:18 am ]
Post subject:  Re: 2009 V358 Generator

Look for a small pop-off access door (~4” x 6”) on the sound box that can be removed without tools. It provides access for impeller replacement without the need of take off the sound box. I usually remove the hose on the discharge side of the pump to remove pieces of broken impeller that can reduce water flow after replacing the impeller.
.
My 2007 Vista has the generator on the Port side. The access door is on the side that faces the bow, which is located by the battery bank. Fairly easy access. I use a Sherwood 8000k impeller kit on my Koehler 5E.

Author:  jnizi [ Sat Mar 10, 2018 9:35 am ]
Post subject:  Re: 2009 V358 Generator

Sounds like the impeller. Very easy replacement.

Author:  captain888 [ Sat Mar 10, 2018 9:55 pm ]
Post subject:  Re: 2009 V358 Generator

Thanks it is not the saltwater impeller have could water flow out the exhaust it just is not circulating the water in the header tank.

Author:  TheDanceII [ Mon Mar 12, 2018 8:49 am ]
Post subject:  Re: 2009 V358 Generator

Have you verified that the closed cooling tank has been properly vented once filled. There is a screw in the top corner of the coolant tank that you remove to allow air to be vented when running. Once coolant flows out, tighten the screw.
That little bit of air will keep the system from running properly and will overheat in about 10 minutes.

Author:  captain888 [ Mon Mar 12, 2018 5:04 pm ]
Post subject:  Re: 2009 V358 Generator

TheDanceII wrote:
Have you verified that the closed cooling tank has been properly vented once filled. There is a screw in the top corner of the coolant tank that you remove to allow air to be vented when running. Once coolant flows out, tighten the screw.
That little bit of air will keep the system from running properly and will overheat in about 10 minutes.


That is my next task is to run it up and bleed that off
Thanks

Author:  TFD2001 [ Tue Mar 13, 2018 6:16 am ]
Post subject:  Re: 2009 V358 Generator

TheDanceII wrote:
Have you verified that the closed cooling tank has been properly vented once filled. There is a screw in the top corner of the coolant tank that you remove to allow air to be vented when running. Once coolant flows out, tighten the screw.
That little bit of air will keep the system from running properly and will overheat in about 10 minutes.



x2

Author:  captain888 [ Tue Mar 27, 2018 1:04 am ]
Post subject:  Re: 2009 V358 Generator

Thanks for that I am going to look at this tomorrow can you tell the correct way to bleed the system can't find it anywhere

Author:  TheDanceII [ Tue Mar 27, 2018 7:33 am ]
Post subject:  Re: 2009 V358 Generator

Open coolant reservoir cap and ensure it is completely toped off.
Install reservoir cap.
Loosen the Bleed Screw.
Crank Generator.
Run until coolant starts to flow out around the Bleed Screw.
Tighten Bleed Screw.
Let Generator run for about 30 minutes to verify.

I have an IR Temp Gauge that I use to verify temp is holding steady at the cylinder heads and coolant reservoir while running.

Author:  captain888 [ Fri Mar 30, 2018 4:55 am ]
Post subject:  Re: 2009 V358 Generator

Thanks guys thanks s fixed the problem but after some running I shut it down went to start it a few hours later now it is coming up with a uu code any ideas.
Tries to start but won’t run but I do need to put fuel in my boat as I am very little w to b fuel

Author:  chris268 [ Fri Mar 30, 2018 6:14 am ]
Post subject:  Re: 2009 V358 Generator

Not sure if the manual i posted earlier is correct, but here is some info from there

Page 18 of the manual states
The generator set shuts down automatically under the fault conditions listed in Figure 2-5 and the controller displays a fault code. The generator set cannot be restarted until the fault condition is corrected and the controller is reset. See Section 2.6.6 to reset the controller after a fault shutdown. The controller resets automatically after a battery voltage fault condition is corrected.

Figure 2.5 is page 19 which includes UU (under voltage)


Page 22 of the manual states (2.6.6)
Resetting the Controller after a Fault Shutdown
Always identify and correct the cause of a fault shutdown before resetting the controller. Use the following procedure to reset the generator set controller after a fault shutdown.
1. Move the generator set master switch to the OFF/RESET position.
2. Disconnect the generator set from the load using the line circuit breaker. See the safety precautions at the beginning of this manual before proceeding.
3. Identify and correct the cause of the fault shutdown. See the safety precautions at the beginning of this manual before proceeding. Refer to Section 4, Troubleshooting.
4. Start the generator set by moving the generator set master switch to RUN. Test operate the generator set to verify that the cause of the shutdown has been corrected.
5. Shut the generator off by moving the generator set master switch to the OFF/RESET position.
6. Reconnect the generator set to the load using the line circuit breaker.
7. Move the generator set master switch to the AUTO position for startup by remote transfer switch, remote start/stop switch, or remote digital gauge.
Opening and closing the remote start/stop contact also resets the controller.


Hope this helps

Author:  captain888 [ Sun Apr 01, 2018 10:20 pm ]
Post subject:  Re: 2009 V358 Generator

All fixed just needed some gas in the tank lol